When your UPS Batteries Fail And You Have A Sold Out Show In Two Hours

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts

  • #16
    Most regenerative UPS's do run on 48 volts including the ones I put in. But in any large broadcast site here you are going to find everything under the sun. From 750 VA to room sized systems. The one in the picture is 2.5 mW capacity and there is a second room about 20 x 30 feet filled with shelves of lead acid batteries. Max run time for 8 DTV transmitters is 30 minutes. Power switches to the UPS and then.they start and warm up the generator for 10 min before switching to it. This is the largest UPS I have encountered. Every theater should have a generator like that...
    Attached Files

    Comment


    • #17
      The digital read out versions of the SMART Tripplites are the only version...they reved the product line and when they did...the problems started with it...just like the pull out keyboards. We never had problems on the 5:4 Tripplite pull out consoles...but once they reved the product into a widescreen version...they rip themselves apart and the trackpads go bad quickly. Everytime Tripplite updates a product, it gets significantly worse.

      APC costs about 10-20% more for the "like" product from Tripplite (their model numbers are VERY close to make it easier to compare) so if APC proves to be problematic, I'll move away from them. So far, so good. Tripplite is certainly easier to mount (less deep) and Tripplite has a better rack mount system than APC.

      Regardless, an ATS will be going in with any UPS I put in.

      Oddly, the cheepie APC UPSes I have at home sourced from Amazon on their "Deal of the Day" have been doing the job (including this morning where we lost power for 5-seconds)...no blips on the computers/DVRs.

      Comment


      • #18
        That explains a lot... All the ones I installed have the bar graph displays. I have a small Tripp Lite regen ups here on my computers, I think 900VA. But not once in two years has the power gone out. Burried cables help.
        Edit: Steve, They still make the UPS, but it's been slightly uprated and has a new model number. IN fact the entire line of double conversion UPS's have been re-done. Still have the same display though.

        https://www.tripplite.com/smartonlin...SAAEgLEhfD_BwE

        Attached Files
        Last edited by Mark Gulbrandsen; 10-13-2020, 12:53 PM.

        Comment


        • #19
          Originally posted by John Thomas
          UPS failures have been hands-down the most common failure I have seen in digital cinema, Doremi power supplies being a close second.
          IMHO, Doremi power supplies have stiff competition from NEC router boards and cat745 certificate batteries (likely because there are a lot of them in the field that never had them changed, and are now getting old enough for the original batteries to fail) for the runner up prize. But agreed that UPS batteries are the clear winner.

          Comment


          • #20
            Originally posted by Leo Enticknap View Post

            IMHO, Doremi power supplies have stiff competition from NEC router boards and cat745 certificate batteries (likely because there are a lot of them in the field that never had them changed, and are now getting old enough for the original batteries to fail) for the runner up prize. But agreed that UPS batteries are the clear winner.
            Only had three original router boards fail, all in NC-2000's. All in really old projectors...

            Comment


            • #21
              I do about three NEC router board swapouts a year. I can't remember doing any in a projector younger than five years, but that appears to be when they start to become unreliable. We also sell around a couple of dozen of them a year for installation by others. They are a frequently enough requested part that we keep them in stock. As with the cat745s, Series 2 NECs have now been in service for long enough that we are now starting to see age-related part failures, I guess.

              Comment


              • #22
                Originally posted by Leo Enticknap View Post
                I do about three NEC router board swapouts a year. I can't remember doing any in a projector younger than five years, but that appears to be when they start to become unreliable. We also sell around a couple of dozen of them a year for installation by others. They are a frequently enough requested part that we keep them in stock. As with the cat745s, Series 2 NECs have now been in service for long enough that we are now starting to see age-related part failures, I guess.
                Leo, at your convenience could you post the PN's for the router and the adapter for it? I need to order another three from you guys soon.

                Thanks!

                Comment


                • #23
                  Mark, you are showing the "SU" series UPS (Smart Online...not the same as the SMART)...those have the optional "LCD" display to them...but the original SMART UPS (same part number too) now all have the digital numeric display that is almost as tall as the unit...those are duds. The LCD option for the SU series is just a couple line display.

                  Comment


                  • #24
                    Originally posted by Steve Guttag View Post
                    Mark, you are showing the "SU" series UPS (Smart Online...not the same as the SMART)...those have the optional "LCD" display to them...but the original SMART UPS (same part number too) now all have the digital numeric display that is almost as tall as the unit...those are duds. The LCD option for the SU series is just a couple line display.
                    Sure looks the same... And same specs. Also a regenerative ups...

                    Comment


                    • #25
                      Originally posted by Mark Gulbrandsen
                      Leo, at your convenience could you post the PN's for the router and the adapter for it? I need to order another three from you guys soon.
                      Will do, the next time I'm in the shop and can have a look at one (likely Thursday or Friday).

                      EDIT - found it on a service report. The NEC part number is BR-CP1400N, and MiT's part number is 00308-01.
                      Last edited by Leo Enticknap; 10-13-2020, 09:40 PM.

                      Comment


                      • #26
                        Originally posted by Mark Gulbrandsen View Post
                        Most regenerative UPS's do run on 48 volts including the ones I put in. But in any large broadcast site here you are going to find everything under the sun. From 750 VA to room sized systems. The one in the picture is 2.5 mW capacity and there is a second room about 20 x 30 feet filled with shelves of lead acid batteries. Max run time for 8 DTV transmitters is 30 minutes. Power switches to the UPS and then.they start and warm up the generator for 10 min before switching to it. This is the largest UPS I have encountered. Every theater should have a generator like that...
                        Yeah, not an uncommon sight. In a previous life, I used to do some contracting work for datacenters. Those kind of setups were pretty common back then. Nowadays, some of those datacenters have grown to proportions where they sometimes even build their own on-site power plants...

                        But as you can see, they keep their battery banks in separate rooms. Back in the days we ran our own datacenter site, where we had the batteries inside the "UPS room" at first. The temperature was always quite high, especially in the summer. Batteries never lasted. Once we moved them into a separate building with some basic climate control, I felt a lot safer and those batteries essentially lasted forever.

                        If I had to chose between putting the batteries or a diesel generator inside the building, I'd actually choose for the diesel generator. Although, those things also come with the necessary precautions. I remember a test-run where the vent to the outside failed to open. The thing sucked the oxygen out of the room and created a vacuum and as a result, we couldn't open the doors to the generator room, until it died of oxygen shortage shortly after. As a result we built a bunch of always-open vents into the room and reversed the way the doors opened. The latter part required a special permit from the local fire brigade, as they wanted doors that opened to the outside. But, imagine being in that room while the machine starts and the vent refuses to open...
                        Last edited by Marcel Birgelen; 10-14-2020, 02:44 AM.

                        Comment


                        • #27
                          Originally posted by Marcel Birgelen View Post
                          Most transmitter sites I know use 24V/48V DC setups. Just like most telco sites, that includes mobile cell sites, which all use (-)48V DC. They use this because the backup power setup is as simple as it gets: Just an array of regular 12V/24V batteries and a charging circuit. Most telco and transmission equipment also comes with 48V PSU options.

                          But yeah, 120/230V AC equipment is creeping in everywhere nowadays...
                          I know what you mean. A friend of mine works in government public safety radio communications, and during a weeklong power outage in the middle of winter, they had to keep the fire/ambulance/police radios running, and because of the lack of generators available, they had to resort to using a set of pickup trucks left running at the tower, with jumper cables from the trucks running into the shack to keep the batteries charged.

                          Comment


                          • #28
                            Originally posted by Justin d'Entremont View Post

                            I know what you mean. A friend of mine works in government public safety radio communications, and during a weeklong power outage in the middle of winter, they had to keep the fire/ambulance/police radios running, and because of the lack of generators available, they had to resort to using a set of pickup trucks left running at the tower, with jumper cables from the trucks running into the shack to keep the batteries charged.
                            Yep! One has to do what ever one can do to keep things running. At the transmitter site above it is atop a mountain with switch back roads going up.One time they had lost power because of a large substation failure down on ground level. So they used the generator for almost a month, and in order to get a fuel truck up there it takes a crane to lift the back end of the truck around each curve. So getting the truck up to 10,000 feet, unloading it's fuel, and then getting it back down around each curve is a two day job.

                            Comment


                            • #29
                              Coming from a server room/data center perspective, I'm honestly surprised that any of this is a problem. Any decent UPS will normally just fault to street power if the batteries fail. It will make loud beeping noises, but the power won't be interrupted (although under/over voltage correction functionality may be lost). The APC SMART-UPS models will definitely do this. I had one of these at home where the battery exploded (the UPS was about 17 years old--well beyond its expected life) and the connected equipment kept working fine. (I'm not super-thrilled with APC hardware in general, but it seems decent enough and their support is excellent.)

                              I like Sean's idea of separate power for redundant equipment. In a data center environment, we would normally have an A feed and a B feed, usually from separate street power grids, with separate UPSes, generators (often one diesel, one natural gas), and transfer switches. A PDU on one side of each rack carries the A power and one on the other side carries the B power. Most IT hardware has dual power supplies, so one power supply connects to each power feed.

                              48v telecom power is also a good idea, although I don't know much about it (I'm not a telecom guy) and wouldn't work for most cinema equipment.

                              Comment


                              • #30
                                I have the APC Smart units with the ethernet card installed in a couple of locations that are hard to get at. They've been quite reliable. I find it's great if you need to do a hard reset of any of the hardware connected to them. I can just log into the UPS and send a reboot command to a specific outlet group. It's been handy for things like remotely upgrading firmware that requires a powercycle to complete the job. I haven't implemented the SNMP features yet to monitor battery performance but it's in queue.

                                Comment