Ian Price
Phenomenal Film Handler

Posts: 1714
From: Denver, CO
Registered: Jun 99


 - posted 04-19-2001 01:09 AM      Profile for Ian Price   Email Ian Price   Send New Private Message       Edit/Delete Post 
At great expense, we ordered 38 compact florescent light bulbs for our lobby. The total cost was somewhere around $950. A compact florescent lamp is supposed to outlast 6 incandescent lamps. The total cost for 228 incandescent PAR 30 lamps would be around $1,150. Of course we didn’t let the 38 incandescent lamps burn out before replacing them. We will use them in the booth where the lights are only one for 15 minutes to one hour at a time. The lights in the lobby are on for 12 hours per day.

38 incandescent PAR 30 lamps at 75 watts would use 2,850 watts of electricity. 38 compact florescent lamps at 15 watts will use 570 watts of electricity.

We are doing this because of the current energy hysteria here in California. In theory we will save just on the cost of lamp replacement. But that theory is blown because we didn’t let the incandescent lamps burn out and thus using their full life. But we also hope to save money by the lobby lights using 20% of the energy that they were using before. Now we don’t expect to see a huge drop in the utility bill because we still have 5 Xenon lamps that can’t be run on less power and we still have 7 HVAC units on the roof and I’m sure they are energy hogs.

But you do what you can.

 |  IP: Logged

Mike Spaeth
Phenomenal Film Handler

Posts: 1129
From: Marietta, GA
Registered: Jul 2000


 - posted 04-19-2001 01:15 AM      Profile for Mike Spaeth   Author's Homepage   Email Mike Spaeth   Send New Private Message       Edit/Delete Post 
My company requires the use of compact flourescents. I haven't seen the numbers side of it, but it makes sense. I have heard from too many people how much money is actually saved from using these, plus the light output is phenominally more.

 |  IP: Logged

Ken Layton
Phenomenal Film Handler

Posts: 1452
From: Olympia, Wash. USA
Registered: Sep 1999


 - posted 04-19-2001 01:28 AM      Profile for Ken Layton   Email Ken Layton   Send New Private Message       Edit/Delete Post 
Remember you can't use them on a dimmer circuit, so you won't be able to use them in the auditoriums.

 |  IP: Logged

Ian Price
Phenomenal Film Handler

Posts: 1714
From: Denver, CO
Registered: Jun 99


 - posted 04-19-2001 01:54 AM      Profile for Ian Price   Email Ian Price   Send New Private Message       Edit/Delete Post 
The lobby is noticeably brighter.

I had to remove a couple of rheostats to install the florescent lamps in the lobby.

Strangely all of the work lights in the booth are on rheostats. When I want work lights I want them on bright!

We will not be using the florescent lamps in the auditoriums.

I have been in one theatre that uses florescent tubes and they are dimmable. It is a rather nice theatre too.

In Washington DC I was in an Art House that used unfiltered, florescent tubes as house lights. When the film was ready to start, bam! Out went the lights. At the end of the feature; Flick, flick, flicker bam, they snapped on. That was ugly.

 |  IP: Logged

Jerry Chase
Phenomenal Film Handler

Posts: 1068
From: Margate, FL, USA
Registered: Nov 2000


 - posted 04-19-2001 08:34 AM      Profile for Jerry Chase   Author's Homepage     Send New Private Message       Edit/Delete Post 
If you have recessed ceiling lights that need to be dimmed, check into the ER (ellipsoidal reflector) bulbs. Depending on the situation, you can often cut the wattage down to 50 watts where a 75 watt or stronger R series bulb is needed.

CFs give wierd light. I hate it when restaurants use these becuase the food looks alien. Some of our house has CF, some has regular flourescent, and some incandescent. I was recently trying to judge color balance on an ink jet photo printout, and drove myself crazy when trying to find the "correct" light to view it in. The CF had a spike that made the green pigment look almost like day-glo.

 |  IP: Logged

Ian Price
Phenomenal Film Handler

Posts: 1714
From: Denver, CO
Registered: Jun 99


 - posted 04-19-2001 04:19 PM      Profile for Ian Price   Email Ian Price   Send New Private Message       Edit/Delete Post 
This morning I came in the theatre and turned an all the lights. When I looked up I was horrified! It's still dark in the lobby. I looked up and saw that the light bulbs were on and just barely glowing. Then the phone started to ring. I handled two telephone calls and by the time I put the phone down, the lamps were almost to full brightness. They seem to take 2 or 3 minutes to warm up.

I haven't noticed that they make the food look any different. After all, it's a florescent tube in the popper and the warmers with a yellow filter on it. The color is cooler than with the incondescent but you would have had to know what it looked like before. I'm sure our local taste police will complain; But he complains about everything. There is just a little bit more glare than before.

But over all, I like it. Ky hasn't seen the full effect yet. I'll be interested in his impressions.

 |  IP: Logged

Greg Borr
Film Handler

Posts: 39
From: Watervliet, MI
Registered: Mar 2000


 - posted 04-19-2001 04:22 PM      Profile for Greg Borr   Author's Homepage   Email Greg Borr   Send New Private Message       Edit/Delete Post 
Compact Fluorescent's have come a long way, the newer electronic C.F's can be dimmed, but not with a traditional dimmer. You have to purchase a C.F. dimmer.

As for weird light, depends on the lamps you have selected, compact fluorescent and all fluorescent lamps for that matter are avaialable in several different varieties. For general lighting purposes I would suggest selecting a lamp that has a 4100K color temperature and is above 80cri (color rendering index)

The original C.F.'s were 2700K and 70CRI, with electromagnetic ballasts that caused flickering. Not only was this annoying, but you couldn't see a whole lot under this light. Alot of these lamps are still being produced and sold as bargains, so buyer beware.

Fluorescent lighting when applied correctly can be not only a cost savings but a better lighting technolgy all together.

Greg Borr
Ready Theatre Systems

 |  IP: Logged

Mark Gulbrandsen
Resident Trollmaster

Posts: 16657
From: Music City
Registered: Jun 99


 - posted 04-19-2001 06:03 PM      Profile for Mark Gulbrandsen   Email Mark Gulbrandsen   Send New Private Message       Edit/Delete Post 
Indeed there are a number of ballasts that can be dimmed quite easily. Advance makes at least three different ballasts that are capable of dimming. I have installed and programmed allot of dimming systems in Universitys and buildings that are completely florescent based. The new underground library at Brigham Young University is almost all dimmable florescent and that place has at least 2000 fixtures!
However...The big problem is fading them down and out. Most dimmer controlers and or ballasts will pop off when you reach the 15 to 20% level. This looks tacky to say the least. Cineplex has also used allot of dimmable florescent systems in their auditoriums. They are marginal as far as performance goes. This may be due to the older dimmer designs that I have seen them installing. The other problem is that with certain ballasts the lamps have to be aged in for 40 to 60 hours before they will dim properly and not ageing them in can cause very shortened lamp life. That can create a customer usage problem and cause confusion when rooms are re-lamped.
Strides are being made with this field but IMHO it is still not suitable for use in Motion picture auditoriums.
Lobbies and other areas however should make full use of these technologies to conserve what ever energy they can. Lamps that are on for long hours will benefit most from this sort of arrangement.
Mark @ GTS


 |  IP: Logged

Josh Jones
Redhat

Posts: 1207
From: Plano, TX
Registered: Apr 2000


 - posted 04-19-2001 08:15 PM      Profile for Josh Jones   Author's Homepage   Email Josh Jones   Send New Private Message       Edit/Delete Post 
The Fargo Theatre installed dimmable fluorescent tubes in the auditorium. They dim nice until about 30% then pop, black. Its worse when they come on. flick-flick-flick-ting-FLASH. they start at about 50%. when they were first installed, they had problems staying lit at half house, which is used for credits. The auditorium also has neon, which is extinguished instantly when the projector starts. for those who are currious I shall post a pic.

cool, huh?

Josh


 |  IP: Logged

Joe Schmidt
Expert Film Handler

Posts: 172
From: Billings, Montana, USA
Registered: Apr 2001


 - posted 04-19-2001 09:33 PM      Profile for Joe Schmidt   Email Joe Schmidt   Send New Private Message       Edit/Delete Post 
Wait, wait, wait, just a minute here. I tink so ALL youse guys has forgotton that if you run incandescent lamps on direct current, slightly lower than rated voltage, the life is extended substantially, especially if you ALWAYS dim them up and down, never switch abruptly. And it's easy to build. Start with a motorized autotransformer dimmer made by whoozits [I forget name] add on big diodes and capacitors and you're there.

This is especially good if you have house lights which are hard to get to for bulb replacement. You wait for one or two to burn out then get the scaffold in and replace them all at once then it's good for several years again.

It's splitting hairs to worry about electricity used by house lights which aren't on that much compared with what the projector xenon lamps use and you can't cut back on that!

 |  IP: Logged

Aaron Sisemore
Flaming Ribs beat Reeses Peanut Butter Cups any day!

Posts: 3061
From: Rockwall TX USA
Registered: Sep 1999


 - posted 04-19-2001 11:50 PM      Profile for Aaron Sisemore   Email Aaron Sisemore   Send New Private Message       Edit/Delete Post 
Also be aware that some of the CF units are not designed to be installed in recessed fixtures or inverted at all!!! We found this out the hard way with about 20 CF units that were all dead from overheating in less than 2 days just before the theatre was to open

I like the idea of using DC for incandescent fixtures, especially those that get dimmed a lot. Wonder how I can get (or make) some kind of DC supply to do this made that won't be an occupational hazard....

Aaron

 |  IP: Logged

Mike Blakesley
Film God

Posts: 12767
From: Forsyth, Montana
Registered: Jun 99


 - posted 04-24-2001 01:13 PM      Profile for Mike Blakesley   Author's Homepage   Email Mike Blakesley   Send New Private Message       Edit/Delete Post 
Josh, that's a great auditorium. How many seats? Does it have a balcony?


 |  IP: Logged

Tom Sauter
Expert Film Handler

Posts: 163
From: Buffalo, NY, USA
Registered: Sep 2000


 - posted 04-24-2001 05:31 PM      Profile for Tom Sauter   Author's Homepage   Email Tom Sauter   Send New Private Message       Edit/Delete Post 
I just improved the lighting in two theatres originally equipped with recessed Par 38 fixtures. Even with the maximum 150 Watts per fixture the light only goes straight down. I installed 75 watt halogen wide angle ellipsoidal reflector floods with a few socket extensions to bring the face of the lamp almost flush with the ceiling.

We now use 50% of the electricity and my light meter says we're 3 times brighter (and evenly lit)!

If you're concerned about strange color temperatures from CF's try some Rosco CTO gels like 3409 or 3408 to balance with incandescent fixtures. Tape into a tube and slide over ... watch out for hot parts of the fixture which will quickly undo your work. We use the same trick to balance Xenon followspots with halogen stage lighting.


 |  IP: Logged

Josh Jones
Redhat

Posts: 1207
From: Plano, TX
Registered: Apr 2000


 - posted 04-24-2001 05:41 PM      Profile for Josh Jones   Author's Homepage   Email Josh Jones   Send New Private Message       Edit/Delete Post 
The fargo seats 870 including balcony which is 20 or 30 seats less than they had before the remodel. I volenteered projection for 3 years on weekend and show up on occasion for late night shows. This Friday 11:30 is Pulp Fiction!
www.fargotheatre.com/

Josh


 |  IP: Logged

Paul Konen
Jedi Master Film Handler

Posts: 981
From: Frisco, TX. (North of Dallas)
Registered: Jun 99


 - posted 04-25-2001 10:02 AM      Profile for Paul Konen   Email Paul Konen   Send New Private Message       Edit/Delete Post 
Ian, I have noticed the same thing about the lights "warming" up.

We have them installed in our booth and they do the same thing, turn on and warm up to full brightness.

Paul.

 |  IP: Logged



All times are Central (GMT -6:00)
This topic comprises 2 pages: 1  2 
 
   Close Topic    Move Topic    Delete Topic    next oldest topic   next newest topic
 - Printer-friendly view of this topic
Hop To:



Powered by Infopop Corporation
UBB.classicTM 6.3.1.2

The Film-Tech Forums are designed for various members related to the cinema industry to express their opinions, viewpoints and testimonials on various products, services and events based upon speculation, personal knowledge and factual information through use, therefore all views represented here allow no liability upon the publishers of this web site and the owners of said views assume no liability for any ill will resulting from these postings. The posts made here are for educational as well as entertainment purposes and as such anyone viewing this portion of the website must accept these views as statements of the author of that opinion and agrees to release the authors from any and all liability.

© 1999-2020 Film-Tech Cinema Systems, LLC. All rights reserved.