Author Topic: Xenon Lamps--Toxic?
Michael Elam
Film Handler

Posts: 84
From: Clarksville, IN, USA
Registered: Mar 2001


 - posted 10-27-2004 04:49 PM      Profile for Michael Elam   Email Michael Elam   Send New Private Message       Edit/Delete Post 
I have a city inspector insisting that we move exhaust systems
claiming the Xenon lamps produce toxic chemcials. He's not satisifed with documents that show UL approved and 'ozone-free', does anyone have a document that will clearly state they are NOT toxic?

 |  IP: Logged

Aaron Sisemore
Flaming Ribs beat Reeses Peanut Butter Cups any day!

Posts: 3061
From: Rockwall TX USA
Registered: Sep 1999


 - posted 10-27-2004 06:27 PM      Profile for Aaron Sisemore   Email Aaron Sisemore   Send New Private Message       Edit/Delete Post 
Aside from any ozone and UV radiation produced by operating a xenon lamp, the only other 'toxic' material related to xenons would be the traces of thorium in the electrodes, but that would only apply if the bulb were broken and you tried consuming the electrodes [puke] there is no real threat to the public from proper operation of a xenon lamp.

-Aaron

 |  IP: Logged

Gordon McLeod
Film God

Posts: 9532
From: Toronto Ontario Canada
Registered: Jun 99


 - posted 10-27-2004 06:37 PM      Profile for Gordon McLeod   Email Gordon McLeod   Send New Private Message       Edit/Delete Post 
technically the UL approval on most xenon lamphouses specifies that they be vented to the outdoors

 |  IP: Logged

Michael Elam
Film Handler

Posts: 84
From: Clarksville, IN, USA
Registered: Mar 2001


 - posted 10-27-2004 07:06 PM      Profile for Michael Elam   Email Michael Elam   Send New Private Message       Edit/Delete Post 
This inspector is wanting us to move the exhaust for 8 consoles,
that have been in place for 15 years, he is claiming that the
exhaust are too close to the HVAC units and that 'toxic' fumes
from the exhausts are being allowed to enter the HVAC units, he wants the exhausts moved 10 feet or 'lifted' two feet above the
height of the HVAC unit. [sleep]

 |  IP: Logged

Marc Hansen
Film Handler

Posts: 93
From: Seattle, WA, USA
Registered: Dec 2000


 - posted 10-27-2004 08:56 PM      Profile for Marc Hansen   Email Marc Hansen   Send New Private Message       Edit/Delete Post 
Ask the inspector(politely)to give you a copy of the regulation he wants you to comply with. Either he won't be able to come up with it (problem solved),or he will and you will know what info you need to counter it, or you'll know there is no way out and you have to change it. I learned this from my fire inspector. A new, young inspector came thru my business and found 16 "violations". I went to the senior inspector, asked him about it(he had inspected my many times before), he just shook his head and said "make him prove it". It came back a few weeks later with just 2 items listed (absolutly valid). The inspectors can't be current on everything, there is just too much. Treat them right, respect them and they can be an asset to your business. The young inspector now comes thru my business points things out and signs off the form. He knows anything valid will be fixed.

 |  IP: Logged

Mark Gulbrandsen
Resident Trollmaster

Posts: 16657
From: Music City
Registered: Jun 99


 - posted 10-27-2004 09:06 PM      Profile for Mark Gulbrandsen   Email Mark Gulbrandsen   Send New Private Message       Edit/Delete Post 
This guy has definately been smoking some of that I-15 stuff!!!

But really, take the advice and ask him, in writing only via certified mail that only he can sign for, for a copy of the regulation so you can study it in great detail. By mailing him the request you have proof that you asked him for it and he must provide it. If they get you on non-compliance and he never provided you with the correct info after wrigint the request you can prove that it was requested.

On a new job in Southern Utah the new local inspector wanted the safety data on every piece of equipment going into the building. Getting it together wasn't that big of deal and we gave him a basket full of info and documents to keep him busy.

Another job in progress is only a half block from the local OSHA office... that ought to be interesting.

Mark

 |  IP: Logged

Michael Elam
Film Handler

Posts: 84
From: Clarksville, IN, USA
Registered: Mar 2001


 - posted 10-29-2004 06:35 AM      Profile for Michael Elam   Email Michael Elam   Send New Private Message       Edit/Delete Post 
Looks as if we are going to move the exhaust, we admitted he was new, as well he admitted the codes are very old and mostly
likely written for the carbon arc days, but he insists as long as it is code then we must move them.

 |  IP: Logged

Frank Angel
Film God

Posts: 5305
From: Brooklyn NY USA
Registered: Dec 1999


 - posted 10-29-2004 07:05 AM      Profile for Frank Angel   Author's Homepage   Email Frank Angel   Send New Private Message       Edit/Delete Post 
If that is the case, and you feel the regulation is outdated and you have been operating for 15yrs with other inspectors not citing you, and especially if other similar regulations are still on the books that pertain to long abandoned methods of operations (such as those relating to nitrate film use), you can present a prima facia case that the regulation is obsolete and you are demanding a variance from the city regulatory agency, whichever it is that administers those codes.

More than likely this same thing has been done for a variety of regs as would have to have been the case when platters came in to use; there were all kinds of regulations governing how much (or rather how little) film was allow exposed to air in the booth, how many total number of feet of film could be contained in the booth at one time....etc. Those regs may never have been revoked but somewhere along the line, some exhibitor or big chain got a variance so they could put in a platter. Same with fire walls, fire shutters, etc. I would guess that most new builds don't have fire shutters and certainly they don't have double fire walls that isolated the booth from the theatre proper. When single screens began to be routinely converted into those hideous multiplexes, all those old regs went bye-bye. The fire regs and building codes that were written to protect theatres from the hellish evils of nitrate stock were either quickly revised or variances were obtained so they could be legally ignored. I am sure you could get the same for this foolish reg about exhaust stacks.

Check out other booths. If a big chain has a similar "violation" that has been ignored by the inspectors, that would be a very good addition to any plea for variance or to actually get the code revised. If say a Sony Theatre booth has the same condition, you might be able to get the big guns to go in on a petition to get the reg altered or completely removed from the code books. And if they are not interested in helping you, you could still name them and claim unfair hardship is being directed only at you which would be a restraint of trade and unfair practice. But usually exhibitors would find it to be in their own best interest to get changed in their favor. You might find yourself standing up there along side a slew of big chain lawyers. And be sure of this....the bigger the cat making the hissing sound, the quicker the bureaucRATs sit up and take notice!

 |  IP: Logged

Darryl Spicer
Film God

Posts: 3250
From: Lexington, KY, USA
Registered: Dec 2000


 - posted 10-29-2004 08:06 PM      Profile for Darryl Spicer     Send New Private Message       Edit/Delete Post 
Hell, I worked in a theater for 7 1/2 years were all the exhaust was emmitted into the projection booth. Four of the projectors were located in the lobby. Hell there is probably more toxic fumes in the actual air it's self than will ever be emitted from a xenon bulb. The codes need to be re-written for non-carbon arc facilities otherwise we are being forced to have to pay for something that is not needed.

It needs to be taken to court or something before one dime is spent on any changes.

 |  IP: Logged

Jason Black
Phenomenal Film Handler

Posts: 1723
From: Myrtle Beach, SC, USA
Registered: Nov 2000


 - posted 10-29-2004 09:39 PM      Profile for Jason Black   Author's Homepage   Email Jason Black   Send New Private Message       Edit/Delete Post 
Daryl,

Taking the case to court will require greater expenditures than paying the HVAC crew to extend the vent tubes the extra 2' they need to be moved.

While I agree with your feeling that certain codes should allow for what I call 'common sense' variances, it is often an unwise choice to question a code inspector. I witnessed a pissed off electrical inspector state that a theatre (3 days from opening) would require further inspection after a frosty machine (of all things) was found with no UL label. At that point, he demanded to see UL labels on ALL electrical equipment in the building. He wanted to see it immediately, or he would be back for further inspection "when he could get to it". This is the same A-hole who took out a neutral screw from the main breaker panel, looked at it, then measured it to see if it was the proper length. Thank God it was at least green, as code required.

Bottom line, as someone else already stated, treat the person with soem respect, not with an attitude, and you'll generally be ok. I had a friend who owns a restaurant (among many other things)... The health dept. came around for routine inspection. Just so happened that my friend knew that the inspector was recently 'estranged' from his wife... so what does he do? Asks how the wife is.... LOL... Needless to say, 6 years later, he STILL catches grief on all his inspections...

 |  IP: Logged

Steve Kraus
Film God

Posts: 4094
From: Chicago, IL, USA
Registered: May 2000


 - posted 10-29-2004 09:52 PM      Profile for Steve Kraus     Send New Private Message       Edit/Delete Post 
What is the legality of requiring anything from UL, a private company?

 |  IP: Logged

Darryl Spicer
Film God

Posts: 3250
From: Lexington, KY, USA
Registered: Dec 2000


 - posted 10-29-2004 11:05 PM      Profile for Darryl Spicer     Send New Private Message       Edit/Delete Post 
True it would problaby cost more to get the code changed but if more than one location ends up having the same issues then what happens with the cost.

 |  IP: Logged

Jon Miller
Jedi Master Film Handler

Posts: 973
From: San Diego, CA, USA
Registered: Sep 1999


 - posted 10-30-2004 09:15 AM      Profile for Jon Miller   Email Jon Miller   Send New Private Message       Edit/Delete Post 
quote: Jason Black
...he demanded to see UL labels on ALL electrical equipment...
What about "ETL" certification, which some manufacturers obtain as an alternative to UL certification? That inspector could be excessively anal...

 |  IP: Logged

Dominic Espinosa
Phenomenal Film Handler

Posts: 1172
From: Boulder Creek, CA.
Registered: Jan 2004


 - posted 10-30-2004 11:23 AM      Profile for Dominic Espinosa   Email Dominic Espinosa   Send New Private Message       Edit/Delete Post 
How was the conclusion reached that there's toxic fumes being vented into the building via the HVAC units from the xenon exhausts?
Could he show that there were fumes coming from the vents?
Moreover, if there isn't, what proof does he have that nothing but hot air is escaping from there?

 |  IP: Logged

Gordon McLeod
Film God

Posts: 9532
From: Toronto Ontario Canada
Registered: Jun 99


 - posted 10-30-2004 01:02 PM      Profile for Gordon McLeod   Email Gordon McLeod   Send New Private Message       Edit/Delete Post 
Actually part of the issue isn't that it is the projector exhaust but probably an exhaust from the buiding and there is codes regarding the distance between a fresh air intake and any form of exhaust vent from within the building

 |  IP: Logged



All times are Central (GMT -6:00)
This topic comprises 2 pages: 1  2 
 
   Close Topic    Move Topic    Delete Topic    next oldest topic   next newest topic
 - Printer-friendly view of this topic
Hop To:



Powered by Infopop Corporation
UBB.classicTM 6.3.1.2

The Film-Tech Forums are designed for various members related to the cinema industry to express their opinions, viewpoints and testimonials on various products, services and events based upon speculation, personal knowledge and factual information through use, therefore all views represented here allow no liability upon the publishers of this web site and the owners of said views assume no liability for any ill will resulting from these postings. The posts made here are for educational as well as entertainment purposes and as such anyone viewing this portion of the website must accept these views as statements of the author of that opinion and agrees to release the authors from any and all liability.

© 1999-2020 Film-Tech Cinema Systems, LLC. All rights reserved.