Paul G. Thompson
The Weenie Man

Posts: 4718
From: Mount Vernon WA USA
Registered: Nov 2000


 - posted 10-16-2001 12:48 AM      Profile for Paul G. Thompson   Email Paul G. Thompson   Send New Private Message       Edit/Delete Post 
I have two TA-10's that will not sound the built-in alarm when the projector shuts down for no apparent reason, although I would suspect the film presence or film motion detectors would be causing the shut-down. The reason why I think this is because the shutdown problem goes away after I straighten out the lower guidance hardware that was wanged out of position by a club-footed projectionist dancing on the film path.

However, the alarm will sound on tail-out if the detector misses the shut-down cue.

Any suggestions as to why the alarm does not sound when a fault is detected? The alarm sounds ONLY if the film tails-out.

 |  IP: Logged

Ken Layton
Phenomenal Film Handler

Posts: 1452
From: Olympia, Wash. USA
Registered: Sep 1999


 - posted 10-16-2001 01:11 AM      Profile for Ken Layton   Email Ken Layton   Send New Private Message       Edit/Delete Post 
Old firmware/software?

 |  IP: Logged

Paul G. Thompson
The Weenie Man

Posts: 4718
From: Mount Vernon WA USA
Registered: Nov 2000


 - posted 10-16-2001 01:14 AM      Profile for Paul G. Thompson   Email Paul G. Thompson   Send New Private Message       Edit/Delete Post 
Ken, I don't know. How do I tell? Supposedly, these were new units as of August of this year.

Paul

 |  IP: Logged

Bill Purdy
Expert Film Handler

Posts: 139
From: Seattle, WA
Registered: Oct 1999


 - posted 10-16-2001 12:02 PM      Profile for Bill Purdy   Author's Homepage   Email Bill Purdy   Send New Private Message       Edit/Delete Post 
Paul, please call Don Olson at 206-284-9171 with your symptoms. He is very good at this sort of thing and will help you get to the bottom of it without a lot of guesswork.

------------------
Bill Purdy
Component Engineering

 |  IP: Logged

Paul G. Thompson
The Weenie Man

Posts: 4718
From: Mount Vernon WA USA
Registered: Nov 2000


 - posted 10-16-2001 03:03 PM      Profile for Paul G. Thompson   Email Paul G. Thompson   Send New Private Message       Edit/Delete Post 
Thank you for the feedback, Bill.

Paul

 |  IP: Logged

Paul G. Thompson
The Weenie Man

Posts: 4718
From: Mount Vernon WA USA
Registered: Nov 2000


 - posted 11-10-2001 05:23 PM      Profile for Paul G. Thompson   Email Paul G. Thompson   Send New Private Message       Edit/Delete Post 
Although I never was able to follow up on Bill Purdy's recommendation, I think I found the cause.

House No. 2 and 3 were shutting down at exactly the same time. The only thing these houses have in common is the 3 phase power.

The problem may be caused by dirty power. It appears when the booth's A/C cycles, it takes the booth lighting into a dip. The power dip lasts about 200 milli-seconds, enough to almost extinguish some of the flourescent lights in the secure areas. I don't think two of the automations like it.

Paul


 |  IP: Logged

Richard Tucker
Film Handler

Posts: 15
From: Austin, TX, USA
Registered: Apr 2001


 - posted 11-10-2001 10:10 PM      Profile for Richard Tucker   Email Richard Tucker   Send New Private Message       Edit/Delete Post 
Are the units hooked up for interlock? If so, check the address on the dip switches. I had a theater that was wired for interlock, but the switches were never set so when one machine shut down, so did several others.
I would not have found this without Don Olsen, and I strongly suggest you talk to him if you still have problems. He has saved my butt on many occasions!!

 |  IP: Logged

Paul G. Thompson
The Weenie Man

Posts: 4718
From: Mount Vernon WA USA
Registered: Nov 2000


 - posted 11-12-2001 04:16 PM      Profile for Paul G. Thompson   Email Paul G. Thompson   Send New Private Message       Edit/Delete Post 
Richard, the system is not interlocked. The only connection common to the two automations is primary power, and nothing else. And, yes, I will get in contact with Don Olson.


 |  IP: Logged

Paul G. Thompson
The Weenie Man

Posts: 4718
From: Mount Vernon WA USA
Registered: Nov 2000


 - posted 11-13-2001 08:24 PM      Profile for Paul G. Thompson   Email Paul G. Thompson   Send New Private Message       Edit/Delete Post 
I spoke with Don Olson, and he also thinks it may be something "cycling" in the building's electrical system. There are a few more things to check. I am confident I will get this problem resolved, and when I do, I will post it for you all.

 |  IP: Logged



All times are Central (GMT -6:00)  
   Close Topic    Move Topic    Delete Topic    next oldest topic   next newest topic
 - Printer-friendly view of this topic
Hop To:



Powered by Infopop Corporation
UBB.classicTM 6.3.1.2

The Film-Tech Forums are designed for various members related to the cinema industry to express their opinions, viewpoints and testimonials on various products, services and events based upon speculation, personal knowledge and factual information through use, therefore all views represented here allow no liability upon the publishers of this web site and the owners of said views assume no liability for any ill will resulting from these postings. The posts made here are for educational as well as entertainment purposes and as such anyone viewing this portion of the website must accept these views as statements of the author of that opinion and agrees to release the authors from any and all liability.

© 1999-2020 Film-Tech Cinema Systems, LLC. All rights reserved.